Marine Air Sys VRP16K
- Cork the Whine
- Scurvy Dog

- Posts: 22
- Joined: May 18th, 2020, 3:23 pm
- Vessel Info: 1997, 355AC
- Location: Sturgeon Bay
- Has thanked: 20 times
- Been thanked: 11 times
- tomschauer
- Admiral

- Posts: 2323
- Joined: March 28th, 2016, 10:52 pm
- Vessel Info: 1998 Carver 355
Suspicious Fishes !
2022 Kawasaki 310X - Location: upper chesapeake bay
- Has thanked: 326 times
- Been thanked: 602 times
Re: Marine Air Sys VRP16K
A lot of good ideas here, but if the unit isn't turning on the water pump on a call for cooling, it is hopefully just the controller, or better yet the controller set up.
Make sure its set for auto fan and cooling mode. Drop the set point a few degrees below room temp and see if it fires up.
if not, I would swap controllers before you dig too deep into the compressor, as the water pump should run even if the compressor is failed or locked out.
Make sure its set for auto fan and cooling mode. Drop the set point a few degrees below room temp and see if it fires up.
if not, I would swap controllers before you dig too deep into the compressor, as the water pump should run even if the compressor is failed or locked out.
- Cork the Whine
- Scurvy Dog

- Posts: 22
- Joined: May 18th, 2020, 3:23 pm
- Vessel Info: 1997, 355AC
- Location: Sturgeon Bay
- Has thanked: 20 times
- Been thanked: 11 times
Re: Marine Air Sys VRP16K
Good afternoon all! So I really apprecaite all the ideas and thoughts. Before I go on.... if anyone reads this please deenergize power to your A/C unit before any troubleshooting!!
After turing the power off to the unit at the circuit breaker and turning off the water pump circuit breaker. I checked the resistance of the klixon (checked ok, normally closed open), the high pressure switch (checked ok,normally closed to open). I then shorted the run capacitor and tested the capicator (checekd ok 25mfd). I then isolated the compressor motor and performed resistenace checks of the motors windigs (checked ok- there was some resistance). I called Marine Air Systems (Domectic) and requested the motors resistance data, they couldn't or wouldnt supply that data..... know a bit a electric motors some resistance is a good thing.
I connected everthing back up, took a look a the wiring diagram and determined that if I piggy backed Comp L1 to L1, and Comp L2 to L2, I could force the compressor to run and determine if the motor was good. I did the piggyback and briefly turned the unit CB on and I heard that beautiful humm and when I turned if off I heard the motor rotor wind down. OK so the compressor is good. (THIS WAS GREAT NEWS!)
With everything deenergized again, I lifted the units control board.... found the issue. Therewas a 5VDC, 30Amp single pole relay soldered on the board that allows the pump and compressor to run when energized, the relay gave up the ghost, there was a burnt pin and when I unsoldered relay and cut it open the contacts in the realy were shot (one too many cycles).
Found the board number, googled it and I found an updated replacement board on line. I ordered it from Wright Marine in the Tampa Area. Wayne is the BEST, great serviceand responsive, parts turn around was exceptional, I cant give this company enough KUDOS. Just fantastic. The retrofit kit for my AC unit is a Marine Air Passpot II to Passport I/O. The kit includes a new control board and a new unit controller, super, super easy to install.
Close the books on this one. Thanks for all the help!! Truly apprecaite it.
It's 85 outside and my salon is now a cool 72 after replacing the board. I truly apprecaite all hte suggestions, close the books on this one.
After turing the power off to the unit at the circuit breaker and turning off the water pump circuit breaker. I checked the resistance of the klixon (checked ok, normally closed open), the high pressure switch (checked ok,normally closed to open). I then shorted the run capacitor and tested the capicator (checekd ok 25mfd). I then isolated the compressor motor and performed resistenace checks of the motors windigs (checked ok- there was some resistance). I called Marine Air Systems (Domectic) and requested the motors resistance data, they couldn't or wouldnt supply that data..... know a bit a electric motors some resistance is a good thing.
I connected everthing back up, took a look a the wiring diagram and determined that if I piggy backed Comp L1 to L1, and Comp L2 to L2, I could force the compressor to run and determine if the motor was good. I did the piggyback and briefly turned the unit CB on and I heard that beautiful humm and when I turned if off I heard the motor rotor wind down. OK so the compressor is good. (THIS WAS GREAT NEWS!)
With everything deenergized again, I lifted the units control board.... found the issue. Therewas a 5VDC, 30Amp single pole relay soldered on the board that allows the pump and compressor to run when energized, the relay gave up the ghost, there was a burnt pin and when I unsoldered relay and cut it open the contacts in the realy were shot (one too many cycles).
Found the board number, googled it and I found an updated replacement board on line. I ordered it from Wright Marine in the Tampa Area. Wayne is the BEST, great serviceand responsive, parts turn around was exceptional, I cant give this company enough KUDOS. Just fantastic. The retrofit kit for my AC unit is a Marine Air Passpot II to Passport I/O. The kit includes a new control board and a new unit controller, super, super easy to install.
Close the books on this one. Thanks for all the help!! Truly apprecaite it.
It's 85 outside and my salon is now a cool 72 after replacing the board. I truly apprecaite all hte suggestions, close the books on this one.
- g36
- Admiral

- Posts: 2115
- Joined: April 7th, 2014, 6:07 pm
- Vessel Info: 1997 Carver 405
- Location: Soddy Daisy TN.
- Has thanked: 7 times
- Been thanked: 654 times
Re: Marine Air Sys VRP16K
Great you got it fixed and also thank you for posting your findings to the forum.
1997 Carver 405
Crusader xli
The Black Pearl
Soddy Daisy Tn.
Crusader xli
The Black Pearl
Soddy Daisy Tn.
-
Viper
- CYO Supporter

- Posts: 6267
- Joined: July 10th, 2015, 9:58 pm
- Vessel Info: 1989 Carver 3807 Aft Cabin
- Location: Ontario, Canada
- Has thanked: 475 times
- Been thanked: 1791 times