You are currently viewing our board as a guest which gives you limited access to view most discussions, articles and access our other FREE features. By joining our free community you will have access to searching the forum topics, post topics, communicate privately with other members (PM), respond to polls, upload your own photos and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

Circuit dropped but breaker did not trip

Discussion of batteries, chargers, wiring, generators, distribution panels, battery switches, etc.
User avatar

Topic author United States of America
AC3207
Scurvy Dog
Scurvy Dog
Posts: 8
Joined: January 27th, 2024, 11:15 pm
Vessel Info: 1986 3207 Aft Cabin
Has thanked: 7 times

Circuit dropped but breaker did not trip

Postby AC3207 » September 22nd, 2024, 9:35 am

Out yesterday on 1986 Carver Aft Cabin. Running generator (Kohler) that has 2 30 amp circuits. One has two ac units on it and nothing else. Running both AC units and all of a sudden they both quit. Checked panel and loss of voltage on that circuit but breaker did not trip. panel seemed fairly warm to touch. Let it cool off for a bit and tried resetting breaker and no voltage still. Once I got back to house hooked shore power up and circuit and ac units work fine. Is this a breaker issue or a generator issue? Thanks.

User avatar

Canada
bud37
Admiral
Admiral
Posts: 4945
Joined: April 23rd, 2015, 10:22 pm
Has thanked: 585 times
Been thanked: 1231 times

Re: Circuit dropped but breaker did not trip

Postby bud37 » September 22nd, 2024, 10:13 am

Your generator only puts out 30 amps total, your boat has that split into two sides ( still only 30amps total ), one for the ac and the other for house loads. When the power went off did you have 120vac power on the house side ? sounds like a generator overload, maybe there was an appliance on and both AC units at the same time, easily done.

Check the breaker on the generator itself if you do not have any power from the gen. ( either side ).
FWIW.....The above is just my opinion..... :popcorn:
User avatar

United States of America
km1125
Admiral
Admiral
Posts: 3524
Joined: February 28th, 2017, 6:04 pm
Has thanked: 72 times
Been thanked: 1055 times

Re: Circuit dropped but breaker did not trip

Postby km1125 » September 23rd, 2024, 3:46 pm

How does it switch the power from using the generator to using shore power? Is that automatic or is there a manual switch. You might have to open things up and look for loose/corroded connections on the AC lines going to that panel.

And panels should not get "warm to the touch" just by using power. That's a big red flag that something needs attention.