Page 2 of 2

Re: Adding a second Air Conditioning Unit to 350 Mariner

Posted: June 8th, 2018, 9:45 am
by km1125
I'm not clear on where your units are mounted. Is one unit significantly higher (on the bridge?) than the other unit?

If so, you may need/want to put a small restriction in the line going to the lower unit so that the flow favors the higher unit. This would be especially true if the lower unit was less capacity than the upper unit.

On measuring the flow: Since you have two outlets, you'll need a friend and two 1 gallon buckets or containers. As the unit runs, fill each container until almost full, then dump out quickly. Record the count and continue to do so for exactly an hour. The only math you need to do is combine the recordings of the two measurements. Simple. :-D

Re: Adding a second Air Conditioning Unit to 350 Mariner

Posted: June 8th, 2018, 12:33 pm
by DesertX
FYI, my factory installed 2 units (16k plus 5k BTU) are both fed from a single 500GPH pump.

Re: Adding a second Air Conditioning Unit to 350 Mariner

Posted: June 8th, 2018, 12:35 pm
by DesertX
FYI, my 2 factory installed units (16,000 + 5,000) are both fed from a single 500 GPH pump.